Mo,
Just a carpenters perspective,
Take a stiff birthday or Christmas card and set it on a table as a "tent" or gable roof. Push down on the ridge, the rafter feet slide out, there's the thrust.
Using a needle and thread make a tie across the bottom and repeat the test. You have made an immutable triangle and proven the tie is in tension since thread doesn't work in compression.
Now move the thread tie halfway up the card and repeat. At the same load the rafters bend and begin to thrust again.
Move the thread up to just under the ridge and load again, I'll bet you have thrust and tear out of the card at the connection.
For the barn in the picture,
If there is just the one tie then it is in tension. In that case the leverage against the tie would make it tough to connect and it would put large bending force on the rafter below the tie. As the tie approaches the plate the forces drop off. I think in the red book it states that a tie should try to be within a foot of the plate. In the IRC rafter span tables it gives a span reduction for conventional rafters as the tie is raised to account for the rafter bending forces.
If you already have a tension tie and then wish to brace the rafters then this raised tie would be in compression. A kingrod with struts might be a better option.
If you do not make a strong triangle of rafters and tie then the ridge should be designed as a beam supporting that section of roof. Yes, the studs are essentially propping the ridge at the gable.
If the tie is below the plate then the thrust from the rafters puts bending forces into the posts, the post is then not just a column in compression it is a column with a combined bending and axial load, this reduces its normal axial load carrying capacity.
Pinegrove's description of the 2 plates with a short section of "tie" between them is neat, never seen that. I guess the pair of beams are helping each other to resist the thrust from building corner to corner. It must be quite flexible to have dropped the new tie, but has obviously held up. I'd sure want a cable or something from rafter foot to foot or turn the pair of plates into a horizontal trussed girder. I guess neither is historic.