I have been doing a considerable amount of thinking and figuring to come up with a possible Timber enclosure/infill system. I should mention that I do not want to use SIP's. Not because I think they are evil or anything like that, but for a number of other reasons, such as: Do not want the full width of timbers encroaching on the interior of the structure; SIPs seem wasteful and expensive to me, along with the associated problems of off-gassing, etc.; SIPs seem to be contrary to the rest of the structure, that is: a timber frame should be (in my opinion) a structure built to last for generations, SIPs do not seem to fit the bill at all. and there's more.

My idea, in it's current form, is:

Timber framed walls (obviously) normally using timbers of a 9" depth. Between the timbers are placed 2x6 studs 2' on center. It is important to note that the framing timbers are between the studs, and not on the 2' spacing. Sheathing is fastened to the outside on the studs, but not fastened to the timbers so that timber movement will not cause sheathing problems. The sheathing is then covered at least with Tyvek or other housewrap, but possibly also with foam panels.

Now on the inside you have a couple of different options. If you desire the inside wall to be flush with the timbers, then you frame it out and plaster/drywall/panel it flush, probably with some sort of trim piece around the timber edges that will hide any movement. The system was originally designed to have about 3 inches of exposed timber on the inside of the structure, and works best like that. In this case you apply plaster drywall or panels to the 2x6 studs, and apply a wooden trim piece to the edge of the timbers (once again to conceal wood movement. This trim piece can be anything, such as a quarter round or a rectangular piece that sits flush with the inside face of the timbers, and is made of the same wood. Think of this is sort of like door or window trim, which is really there to hide a gap.

Now you have a 5 1/2" cavity inside of your walls, and this is where your insulation goes of course.

One last thing, it may also be beneficial to have a v-groove or a cove on the portions of the timber that face into the wall cavities. The purpose of this is so that if the timbers shrink, any air gap will be convoluted, which discourages airflow to some extent. A V-groove would be the more convoluted path, however it might also provide a weak point where the timbers could easily split. A cove would not create the same weakness.

Now I realize that this isn't going to fit with our drams of a super-insulated home. Really, though, the important thing is whether or not it is as good or better than conventional stick framed wall insulation?

This system is intended to provide a reasonable ALTERNATIVE when price is a major factor, and it is also designed so that it can be reasonably executed by non timber framers. I am a fan of traditional means of enclosing the structure, and things such as straw bales. The thing is not everyone will go for those things, at least not yet, and in order to remain viable we must have a reasonable alternative.

If I could, I would build all frames with an infill system similar to Fachwerk, but that would also be expensive, and would only appeal to a limited customer base (which is not a good thing, especially right now)

So what do you think of this idea? Is it viable? Is it good? Is it economical?


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System [Re: D L Bahler] #23783 06/12/10 01:33 AM
Joined: Dec 2007
Posts: 1,882
T
TIMBEAL Offline
Member
Offline
Member
T
Joined: Dec 2007
Posts: 1,882
I think the gap at the post will attract moisture with or with out the v-groove. The inside of the post will be warm and the outside of the post will be cold, allowing repeated condensation when the conditions are ripe. Maybe it is of no concern?

I don't know what the minimal amount of insulation needed on the outside of the post is to stop this from happening.

I keep going to clay and straw or wood chip as an answer, with the post partially buried in the wall of clay/wood chip, say half in and half out, half exposed to the inside of the building and completely covered on the outside, with plaster and render applied.

I am starting to get frustrated with all the options, this is what you get if you want a variable, keep looking.

All the regulations coming down the road is a headache. I will just stay home and work on my gardens and stuff. That is probably what They want anyway.

Define economical?

Not everyone will go for a timbered frame either. Why limit yourself? Where do you draw the line? Rhetorical questions.

Tim

Re: Proposed Enclosure System [Re: TIMBEAL] #23786 06/12/10 02:11 AM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
I am not limiting myself. In fact, I do not limit myself to the extent that timber framing is not the only kind of construction I am involved in. That's right folks, I still will build a stick frame now and then.

As I said, this is just one option. If I had my way I would do all infills of some form or another, like waddle and daub or clay or brick. But not everyone who wants a timber frame would want that. Really if I could I would build all of my building with super wide eaves and half hip roofs, in a bernese Swiss style -but most people probably won't go for that. (that said, the design of my frames is headed in the direction of Swiss framing in a hurry, although the overall appearance remains faithful to American architecture for those who want it to) I can easily see how someone might get the idea that such a system is dirty or crude. It's not my place to push people into buying something they don't want, let's leave that to car salesmen and government officials. Some people obviously have this idea of a slick, trim, clean house and these methods don't fit their picture.

Define economical? Well for this discussion I guess I mean efficient in terms of construction. I want to develop a system that can be executed by people who are not experts at doing it. In other words, I want a way to enclose my walls that can be done by a non timber framer, a non specialized carpenter. This allows me to outsource a lot of work, freeing me up to focus on joinery and things like that. What if I were to build a frame that was to be shipped across the country for example? Would it be a good business practice if I had to ship my workers with it, paying for their hotels, food, etc. not to mention inconveniencing them (and probably myself too) by separating them from their families for a long period of time?
I want a system that can be done by people who don't need paid a lot of money, because they are readily available. -Efficient use of available labor

There is no single answer to the enclosure question in my opinion. It's all a case-by-case thing. I will do things like straw bales and clay and waddle and lime plaster whenever it fits the project and the customer. For example, I am currently building myself a small building for some extra space, this building will be a chance for me to use whatever I want. So what am I doing? I am siding the whole thing with wood, because I am emulating a specific style (one from outside of this country)

The v-groove probably will attract moisture, that is a flaw in the design I know. But will it sweat? Will it result in much heat loss? I thought about having a flexible foam or plastic stip of some sort attach to the post (in lieu of v-groove) or perhaps a series of them. Maybe a plastic half-tube deal with a foam core (just mulling over the idea in my head right now, dont mind my rambling)Something that insulates, is attached rigidly to the post, and can move through or along whatever insulation is there (I am envisioning cellulose)
Another concern is the thermal properties of the post itself. The wooden post has a lower r value than a corresponding cavity filled with insulation, and hardwoods can actually become heat conductors during the winter (as I understand it, the harder the wood the poorer its insulation value)



Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System [Re: D L Bahler] #23797 06/14/10 03:54 AM
Joined: Feb 2010
Posts: 72
C
counselorpaul Offline
Member
Offline
Member
C
Joined: Feb 2010
Posts: 72
My 2 cents: I like the idea of using locally sourced materials as much as possible for all phases of construction. With all the problems related to oil based transport, this can be more sustainable. If the materials are local it is much easier to track down how they were obtained; ie: were they obtained in a responsible manner? Also, aesthetically, local materials simply tend to blend in to the natural environment better than "exotic" materials. For example, a log home looks strange in LA. And an adobe home looks even stranger in Alaska. As an amateur owner builder, local materials can be appealing for several reasons - simple, cheap, efficient, and attractive. Possibly quite labor intensive however (strawbale, adobe, cordwood masonry, etc) So, for the NW use lots of wood - for the SW use lots of soil (adobe).

Re: Proposed Enclosure System #23923 06/24/10 07:57 PM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
Economics is a very important factor to consider when you are building for others, and even more important when you are marketing your services. I can sit here and go on about my ideal system and how it is vastly superior and all that good stuff, but sometimes as businessmen we simply have to compromise.

There is a difference between the owner/builder who is building his own timber frame and has the freedom to use any method he can dream up and the professional timber framer who has to find the balance between quality and cost. That balance is different for every structure and we do well to remember that.

This system I proposed is not intended to be the perfect system with absolute seal and everything else we have dreams about now and then. Rather, this system is designed to be competitive. It is designed to be practical and open up the world of Timber homes to those who would never afford a spacious open design house clad with SIPs, or would never be able to pay me to give them a traditional infill or whatever else you might see as ideal.

SO back to the main point: Aside from the problem of moisture around the post, what other flaws are there that need to be addressed? What is the widest stud spacing I could reasonably use and still clad the inside with drywall? I need to review Indiana building codes again, sigh...


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #23935 06/25/10 05:17 PM
Joined: May 2010
Posts: 8
B
BLAKE1 Offline
Member
Offline
Member
B
Joined: May 2010
Posts: 8
You could try 2x4@24" O.C. on the vertical with a 2x2@16" O.C inside run horizontally with 2" rigid SM foam on the exterior. If you spray foam the 2x4 walls, you'll have approximately an R-35, except at the timbers. But, by spanning the rigid foam on the exterior, to incorporate the infill into the the exterior shell, I don't see anyway that your house wouldn't perform as a 'super-home' based on it's thermal efficiency. Don't forget to tape the rigid foam with sheathing tape and to save money, google tiger foam for DIY application. Do price it out locally first, at least for comparison. To insulate between the posts and the sticks, use friction fit insulation and backer rod to stop convection drafts. Also leave about 1-2" of space between the post and the rigid foam so that movement of that post doesn't buckle your exterior finish.
Hope this gives you some more idea's for your home. Thanks for the tip on the pitch!

Re: Proposed Enclosure System #23951 06/27/10 04:06 AM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
I should clarify. This system is not for me personally. If I were building for myself I would definitely do a 'down and dirty' system, probably with waddle and daub infill between timber posts that are exposed on the outside. This is a system I am trying to develop as an alternative to SIP's for commercial timber framing. It's a part of my long quest to make timber framing available to people that aren't fabulously wealthy. It is my dream to make timber framing something that the common man can afford, because I believe it is something that our society should return to and we will not return to it unless it is available to the majority. (Sorry, I rambled again. just slap me upside the head next time)

Blake, you have some great ideas there. I hadn't thought about having the stud wall offset to the outside of the timbers to have an insulation gap behind the posts! Thanks a lot, that right there solves my biggest problem! Not only that, it allows me to have a little more exposed timber for those who want that look.

The actual insulating material is not so important, that is something that can be decided on a case-for-case basis.

I should also mention that I am a fan of having rigid OSB sheathing on the outside for the sake of nailing and attaching things, like siding. I despise doing remodel work on a house that has only foam or blackboard sheathing and no plywood or anything rigid.

So here is what I am thinking at this point:

Standard Timber Framed structure, with a large space between posts, fully braced so that the frame itself is self-supporting. I.e. it does not rely on sheathing or panels for stiffness and bracing.

The sills and top plates extend past the posts on the outside wall by 2 or 3 inches.

2x6 studs are framed in either 16" or 24" o.c., with the studs placed so that the posts will fall between studs without interrupting their spacing. This can be done easily by starting the stud layout at the outside corner of the sill, since it is out 2 or 3 inches from the post, assuming that the post spacing matches up with the 16" or 24" stud spacing. These studs are lined up with the outside of the sills, so that the exterior wall will be out 2 or 3 inches from the posts, allowing for at least some insulation on 3 sides of the posts.

No sheathing material is applied directly to the timber posts, it is attached to the 9non-structural) studs, and to the sills and plates above and below.

Drywall, lathe ad plaster, or paneling is applied to the interior walls. The cavity between the inside and outside walls can be insulated as if it were a stick framed walls, with the space between the post and exterior wall insulated as well. The insulation material depends on the customer and their budget.

Or option 2, which is what Blake described (option 1 is a hybrid of Blake's idea and my original idea)So I won't repost it, since it was the last post anyway! (I think that would seem kind of disrespectful too)

Both have their advantages, and their disadvantages. I should run up some figures to see which is the winner.

By the way, r-35 sounds pretty good to me!

It seems to me that Blake's idea would make a good super-insulated system, but could potentially be a bit on the expensive side (which isn't always a bad thing either) whereas my modification of the original system, inspired by Blake's idea, might be a bit more affordable (which isn't always a good thing) I think it would be wise to have both as options. I should make up some drawings, because it's always hard to describe things like this with just words...

Thanks again, guys! This is the reason we bring our questions to places like this





Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #23952 06/27/10 04:54 AM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
I have a modification of my design (and then I really need to go to bed)

The spacing between post and exterior wall should be 2", and between the post and the sheathing you should put a piece of 2" foam board. The foam should probably extend past the post edge on either side like 1/4 or 1/2 of an inch or so to ensure a good seal is made.


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #23957 06/27/10 08:27 PM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
Here we are then


picture quality ain't the greatest, but I think you can see everything good enough.

The stuff between the posts and the exterior sheathing can be the good stuff, with like r-7 or r-8 per inch (for a total of around r-15, which is acceptable) or you could use the regular r-5 per inch stuff if you want. fiberglass insulation for a 2x6 wall has an r-value of r-19, so that's the minimum for my system as currently designed. This picture shows studs 16" o.c.


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #23992 07/01/10 04:44 PM
Joined: May 2010
Posts: 8
B
BLAKE1 Offline
Member
Offline
Member
B
Joined: May 2010
Posts: 8
I would leave some room for movement that will occur within the 9x9 over time. I made that mistake once before and when the post started to check (and it didn't take much) the stucco finish cracked and I wasn't very popular with that particular home owner! In lieu of the 2x6 in the corner, you could try a drywallers structural galv. metal corner in order to eliminate the thermal bridging at the corner. Just cut the plumb line at your corner, screw the piece of corner on, and sheet up the other side.
Have you ever tried the Simpson let -in straps instead of sheathing? It's a method that we used instead of sheathing, when we used to build homes with a brick or stone veneer. It's easy to use, effective and saves you a lot of money on sheathing an sheathing labour.
I apologize for the confusion in which home this system is being used for. I build houses for myself from time to time and tend to call everything my home until I pass over the keys!
I'll see if I can get my scanner working and I'll try to post a drawing of what I was trying to describe. Unfortunately, this forum is the extent of my computer ability, but I'll try.

Re: Proposed Enclosure System [Re: BLAKE1] #23993 07/01/10 06:22 PM
Joined: Dec 2006
Posts: 103
D
DKR Offline
Member
Offline
Member
D
Joined: Dec 2006
Posts: 103
If you don't use sheathing, I don't think you'll get an engineer to sign off on your plans, I'd bet. Why not just make your floor 4" wider than your frame and put a full 2x4 wall outside the frame, instead of infilling? It would permit you to slide your drywall behind the posts, and make your stud layout much clearer and easier for everything from sheathing, to siding, to insulation, to drywall.

Re: Proposed Enclosure System #23997 07/02/10 01:47 AM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
Ya, I was not pleased with how the corners were coming out.

About the posts checking, a possible solution could be to either have the sills come out another 1" or 1/2" and so leaving a gap for expansion, or to just use a smaller piece of foam. I don't want the floor to come up too far past the posts, because I do not want the full width of the posts jutting out into the interior, and I don't want to have to use wider than 2x6's, because the extra costs would defeat the purpose of this whole system. This all makes me wonder, how narrow can one go on the posts anyway?

I suppose if I were to have 2x6's 2' OC for the outside sheathing, and then nail 2x2's on the inside horizontally it would bring my walls in a little more. If I would have the sills out a half inch further, then the walls with 2x2's on the inside would be in an inch further than the previous design. I should see whether 2x6's on 2' c. and 2x2's run horizontal on 16" c. would typically require less total wood than just having 2x6's 16" OC.

About sheathing, I want to use sheathing. Like I said, I despise working on houses that don't have any sheathing, because there is nothing to nail to at times when your really need something. It may save money, but to what extent should I apply this idea of saving money?


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System [Re: D L Bahler] #24026 07/08/10 03:18 PM
Joined: Dec 1999
Posts: 171
C
Chris Hall Offline
Member
Offline
Member
C
Joined: Dec 1999
Posts: 171
One minor point - you have used the term 'waddle and daub' several times now. It's not waddle, my friend, its wattle. Waddle is, to quote straight from the dictionary:

1 : to walk with short steps swinging the forepart of the body from side to side

2 : to move clumsily in a manner suggesting a waddle


Wattle, on the other hand, which was the word I believe you were intending, comes from the Middle English wattel, from Old English watel; akin to Old High German wadal: lit. "bandage"

Dating from before 12th century, the word wattle means:

1 a : a fabrication of poles interwoven with slender branches, withes, or reeds and used especially formerly in building

b : material for such construction

c (plural) : poles laid on a roof to support thatch

Hazel switches were a common choice, as far as I know, for wattle in English timber construction.

Please forgive my pedantic language policing, however I am wary of the fact that once that a few people start confusing 'waddle' for 'wattle' in short order everyone will be making the same mistake.

As for your wall system, I'm absolutely with you on the dislike of SIPS. However your system, it seems to me, uses an excess of material to accomplish the structural requirements, given the 2x6 infill studs, and the posts and plates are a major thermal bridge in the wall system you are describing.

Since the wall can be framed entirely with 2x6's and be plenty strong enough to carry the roof, and the timber posts present that thermal bridge, and are only visible on the interior as an inch or three projection, then it seems to me that the timber posts are pretty much superfluous in your system and could be replaced by, dare I say it: trim pieces.

Now, that's not what I would suggest you do, however if you are going to argue for a structural timber frame, then any infill system should be more about providing insulation than about providing structural support - to accomplish that you might consider eliminating the 2x6's and go to some sort of 2x2/2x3 double wall type of infill system, as has been suggested above.

Also, with 9" posts and plates that overhang the posts by 3" or so, as you mentioned above, you end up with pretty massive plates. While I'm not clear on exactly what you are envisioning, if the plate is to be 12" wide then presumably it is at least 8" high? Or are you envisioning a 12x12 plate? That sort of timber is likely to be coming from a halved log at best. or be boxed heart, which will mean that the grain orientation (using green material as you imply) of those sticks will make them prone to cupping across their width, and likely checking pronouncedly as they dry. Such plates would be yet another significant thermal bridge in such a wall system, not to mention a source of air infiltration as they shrink and cup.

Such plates seem, to me at least, a wasteful use of the resource, given that they are excessively large for the structural function of 'wall plate' in a residential application. Wasteful, i.e., 'not economical'.

Since a 2x6 wall by itself would give you that 5.5" cavity for insulation, and would employ dry material with minimal thermal bridging, seems to me the most economical option in comparison to your other plan. All the timber wall elements would add nothing essential in terms of structure, and simply add cost (in terms of labor, materials, and thermal performance losses) - they must be there, it would seem that they do little else than show a few inches of themselves to the interior. Using a 9" thick wall post that is structurally redundant, lowers thermal performance and only reveals 2~3" inside the building seems unwise.

It's good that you are thinking of alternative systems and are considering lots of options and that you are open to critical feedback here on this forum.


My blog on carpentry practice, East and West:

https://thecarpentryway.blog
Re: Proposed Enclosure System #24027 07/08/10 11:45 PM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
In this system, the 2x6's (or whatever they end up being)
are not structural at all, also the extra wide plate does not necessarily ave to be a single timber. You could have your regular timber plate, with a 'fly' extended out attached to the top of the 2x's. The purpose of these 2x's is to support walls sheathing on the outside and drywall on the inside. The idea is inspired by a traditional infill system and is going for that appearance on the inside of the structure.

The actual load bearing structure is a timber frame, it is therefore stronger and more durable than a 2x stud frame, and you don't have to have 8" or 9" of timber on the inside for it to have the beauty of timber. Remember that infilled houses had plaster right up to the edges of the timbers, and often the timbers themselves were plastered or whitewashed over as well.

Now that said, an idea in its earliest forms is very rarely a solid idea, and it's for that reason that I have put it up here.

I have considered the idea of just having a small 2x2 framework on the inside and on the outside with the large cavity in between filled with cellulose or spray foam, But I am not so certain that the cost to the customer would be reduced as a result of using less wood. The reason I say that is because that would require considerably more labor to install, whereas a 2x stud frame between the posts would supply a framework for attaching both the outside and the inside wall coverings.

There are many old barns in my area that use a system quite similar to this, and it is where I have taken some of my inspiration. These barns are true timber frames, often with bents spaced as far as 15 foot apart. However 2x studs are framed between the posts to support the siding. This system was a very common system on old barns and houses alike. The change here is that the studs are moved out a little in my system so that the posts are insulated from the exterior air temperatures.

I have thought a lot about the plates and sills in this system. To have the plates extend full size out 3 inches is excessive, and overly large. But since the stud framework is not structural, the plates could be extended by way of boards that extend past the edges of the timber posts.

And I researched it, 1/2" drywall is can be used with 24" maximum O.C. wall studs, 3/8" must be 16". So with 1/2" drywall, which around here at least is normal for walls anyway, there is no need to provide additional support to the inside.

This system isn't going to be the perfect insulator. It's insulating performance will not be as high as SIPs, I am trying to find and/or develop another system that can do just that. This system is designed to provide an affordable alternative. It is designed for use on a smaller timber framed home, not a timber mansion, the point of which is to allow normal middle class people to have a timber frame. As I have said before, my dream is to open up the world of timber framing to people who cannot currently afford a huge SIP mansion, and who lack the drive, skill or ability to build their own.

For a more thoroughly insulated structure, at a somewhat higher cost, I would definitely prefer the double wall system, with a single large cavity between all posts. This system would provide far superior insulating properties I know, But I think at this point that the extra labor would make it quite a bit more expensive. This other system is I think a reasonable alternative. That said, I am sure that it would be possible to develop a system where the labor costs involved would not be significantly higher.

I am sorry if you got the impression that the stud framing was in any way structural, I assure you that all of the load is born by the timber frame, which the studs are then attached to solely for the purpose of supporting the walls.


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #24028 07/09/10 12:11 AM
Joined: Dec 2007
Posts: 1,882
T
TIMBEAL Offline
Member
Offline
Member
T
Joined: Dec 2007
Posts: 1,882
Here is an interesting link......I like how the larsen truss works. Infill with many choices. http://www.greenhomebuilding.com/articles/larsentruss.htm

I like to know how the house will be heated, if it is local wood cut by the owner and handled by them then they can choose to insulate the house to a lesser degree, if they want to. If Oil or other processed fuel is used than the more insulation the better.

Sometimes it just ain't simple, no way around it. Build a well insulated smaller home, and one story tall. The home in the link is to tall.

Tim

Re: Proposed Enclosure System #24037 07/10/10 01:21 PM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
Interesting

Here in Indiana, heating is likely to be Wood/corn/pellet, Propane/Natural Gas, water source, or electric. No one around here heats with oil anymore (though lots of older houses have oil tanks outside yet) Those new outdoor wood boilers are becoming more and more popular all the time...

I was looking at a pol-built garage the other day and thinkin about how those structures are built. They have their post frame with 2x4's nailed horizontally to the outside on 2 foot spacing with the sheathing then nailed to that. It got me thinking a bit more about the double wall system. I got to thinking that I bet I could very easily make a system that maybe even costs less than framing in studs, and would probably even use less wood, and would certainly insulate better

This system would be to nail horizontal 2x4 or 2x2 nailers to the outsides of the frame, possibly with a a foam barrier between the nailers and the framing members. These are put on 2 foot centers.

On the inside you attach 2x4's directly beside the posts, in or out as much as you want for insulation and timber exposure. You would need 1 or 2 between as well, depending especially on post spacing, so that the wall is stable. To this nailers are attached horizontally, once again 2' O.C. Drywall is supposed to be attached perpendicular to the supports, so it would need to be hung differently than on a stud wall. Make sure whoever hangs the drywall realizes that!



Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #24038 07/11/10 11:09 AM
Joined: Dec 2007
Posts: 1,882
T
TIMBEAL Offline
Member
Offline
Member
T
Joined: Dec 2007
Posts: 1,882
Wood/corn/pellet is just a step below oil and propane in heating sources. They are a complicated process, one in which if you didn't have the refinery you would be left in the cold, pellet plant included. Outdoor wood boilers are wood hogs and inefficient. Anyone with a $10 dollar bow saw could keep warm in the winter, twice. with a simple wood stove. Even in a drafty, not so well insulated house. So why fancy insulated homes? It is attached to the heating sources. and comfort levels.

Tim


Re: Proposed Enclosure System #24039 07/11/10 05:42 PM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
Several people around use have corn stoves. These folks are farmers who raise the corn themselves and have bins full of the stuff anyway. In my opinion, that is a smart idea. Many others have wood stoves, they go out with a chainsaw and cut the stuff themselves. Again, I like that system.

Gas is convenient, I'll say that for it. But gas can be very expensive too. Here we have a major natural gas infrastructure, because the city nearby was built on a very large natural gas deposit. Here in Indiana heating oil never was all that big.

In the city, I would feel safe to say gas is the number 1 method of heating. Out in the country I'd say it's close between wood and propane.

Outdoor wood boilers are inefficient, but they have the distinct advantage of not driving up insurance costs like a regular wood stove does (fire risk) Personally, I would prefer an indoor wood heating system. I have the advantage of being close friends with a heating and cooling expert that I can consult about all these things.



Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Re: Proposed Enclosure System #24041 07/11/10 09:52 PM
Joined: Aug 2009
Posts: 306
C
Cecile en Don Wa Offline
Member
Offline
Member
C
Joined: Aug 2009
Posts: 306
I know that your talking about feed corn but still, in an indirect way it is still food, or potential food, and it strikes me as a shame to be dumping that in the fire in the same way that it doesn't seem right to be using it to fuel autos. And how much energy went into producing that "heating corn"?

Greetings,
Don

Re: Proposed Enclosure System #24099 07/29/10 09:42 PM
Joined: May 2010
Posts: 946
D L Bahler Offline OP
Member
OP Offline
Member
Joined: May 2010
Posts: 946
OK, fine and dandy. The farmer has the right to do with his corn what he wants. As so the consumer has the right to do with it what he wants as well. There's lots of things that can be put toward food that can also be put toward fuel. Do you like biomass furnaces? Well shouldn't you instead compost your biomass for fertilizer to grow food? If corn can be used as a viable energy source (talking about heat, because ethanol is not viable) than it should be. The USA produces an abundance of corn, and our farmers could really use an increase in demand. Farming is not a walk in the park, folks, and it's certainly not a high dollar proposition.

But this is all off of the main topic, which is enclosure...


Was de eine ilüchtet isch für angeri villech nid so klar.
http://riegelbau.wordpress.com/
Page 1 of 2 1 2