Principal Rafter Tie Connection #25033 01/05/11 10:29 PM
Joined: Nov 2006
Posts: 850
mo Offline OP
Member
OP Offline
Member
Joined: Nov 2006
Posts: 850
Howdy,

Since it has been slow, I figured I would show you all one of my funky designs. Its a real doozy, but that's not the reason for showing.

I really want to get some feedback on the joint in the subject line. Now I know with most trusses you would want your compression member (principal rafter) terminating into your tension member (tie beam).

I haven't done that. Without getting too analytical with loads and such, I would like to just get some intuitive feedback. Here is a picture of the bent/truss arrangement:



The Nancy character (think that's her name) gives enough of the scale and span without providing a bunch of dimensions. One other variable would be a common rafter roof system, no purlins landing on the prafters.

I was thinking a through tenon of substantial thickness. A housing in the prafter to give additional bearing on the tie.
Here is a close up of the arrangement:



And another showing the tenon. No tenons were drawn on braces.



What do you think? Has anyone framed like this before?

RSS to the rescue?

Re: Principal Rafter Tie Connection #25034 01/05/11 11:00 PM
Joined: Nov 2003
Posts: 687
G
Gabel Offline
Member
Offline
Member
G
Joined: Nov 2003
Posts: 687
Mo,

First off, nice looking frame. I like the rotated king.

We're doing one like that now, except it's a really low pitch (4 in 12). Looks like a similar span. Required a 1" allthread to handle the tension at the heel.

I know your're trying to avoid a can of worms, but I could be more helpful if I knew the pitch, span, and distance between king posts? Assuming 12 in 12, 24', and 16', you may be able to make the end trusses work with the heel joint you show, but the middle truss will have twice the tension -- quick mental math says 6 or 7 kips at the heel (assuming no snow). Hard to do with pegs. If the span or ridge length is more than that, it's even harder to do.

If I were building it without an engineer's advice (which I wouldn't do of course), I'd use dry wood for the tie, make sure the ends where the tenon is is perfect wood, use perfect wood for the rafters, and put a 2 1/2" thick at least dovetailed thru tenon in it with a wedge below the tie, and try to fit about four 1 1/4" pegs in there. I'd also gorilla glue the wedge.

The dovetail and wedge would be there in case the pegs broke to act as a sort of breaking system so that trouble could be spotted in plenty of time to repair it with ironwork as the joint slowly crept open.


I don't know where the frame is but if it's in snow country you can forget about it.

Also, it'll be wobbly without more bracing. I'm constantly frustrated by how "flexible" timber frames are -- even well cut b


Just my quick thoughts, thanks for posting -- this is fun.

Re: Principal Rafter Tie Connection #25036 01/05/11 11:27 PM
Joined: Jan 2008
Posts: 918
B
bmike Offline
Member
Offline
Member
B
Joined: Jan 2008
Posts: 918
Mo, cool design direction. Without a bunch of data its tough to determine what that joint will be doing. Even in simple span trusses up here in snow country I'm using steel for tension.

I would also consider a moment connection to the piers. You have a lot of roof surface area and not much bracing to take wind loading...

Last edited by bmike; 01/05/11 11:29 PM.

Mike Beganyi Design and Consulting, LLC.
www.mikebeganyi.com
Re: Principal Rafter Tie Connection [Re: bmike] #25039 01/06/11 02:09 PM
Joined: Oct 2009
Posts: 73
Chuck Gailey Offline
Member
Offline
Member
Joined: Oct 2009
Posts: 73
Hey Mo, hard to beat a barrel bolt and some all thread, imo.

I think Mike makes an excellent suggestion about the pier connection, too.


www.otbdesignworks.com


Become a fan of OTB Designworks on Facebook, we'd love to have you
Re: Principal Rafter Tie Connection [Re: Chuck Gailey] #25065 01/07/11 06:26 PM
Joined: Nov 2006
Posts: 850
mo Offline OP
Member
OP Offline
Member
Joined: Nov 2006
Posts: 850
Hey Guys,

Thanks for the feedback. All good ideas and information. Gabel, thanks for your post, it has a lot of good information in there and I appreciate it. You are almost dead on with the dimensioning you proposed. Good eye. I hadn't thought about the effects at the central truss too and twice the load. Thanks.

As far as the connection: A question in regards to the pitch. Am I right in thinking as the pitch becomes greater the thrust is reducing as well. I guess an example (all things being equal and represented as a triangle) as your pitch goes past 12/12 the compression at the heel from the prafter becomes greater than the tension on the tie? Is it true the lesser the pitch the more thrust?

Can engineering problems on this joint come into tolerance by making a pitch greater?

Thanks for yall's contributions.

Re: Principal Rafter Tie Connection #25067 01/07/11 10:10 PM
Joined: Jan 2008
Posts: 918
B
bmike Offline
Member
Offline
Member
B
Joined: Jan 2008
Posts: 918
Higher pitch will reduce outward thrust - but in your design you'll be transferring outward down onto that tenon you drew - which will put it into shear. So you'd likely need some sort of bearing from the p rafters to tie, be sure your tenon is wide enough to handle shearing, and also that the area of the tie over the post can also handle shearing (likely).


Mike Beganyi Design and Consulting, LLC.
www.mikebeganyi.com
Re: Principal Rafter Tie Connection #25074 01/08/11 10:14 AM
Joined: Mar 2002
Posts: 961
K
Ken Hume Offline
Member
Offline
Member
K
Joined: Mar 2002
Posts: 961
Hi Mo,

You could extend the post right up to a shouldered housing cut in the underside of the pricipal rafter and then have the tie beam simply connect to the inboard side of the main post.

Regards

Ken Hume


Looking back to see the way ahead !
Re: Principal Rafter Tie Connection #25075 01/08/11 11:48 AM
Joined: Jan 2008
Posts: 918
B
bmike Offline
Member
Offline
Member
B
Joined: Jan 2008
Posts: 918
Ken - I think the danger with that approach has similar concerns with raiding the pitch - you end up potentially shearing the top of the post off instead of the end of the tie. (but remember that I live and work in snow country...)

Whichever direction it takes I'm sure Mo will analyze it for his local conditions.


Mike Beganyi Design and Consulting, LLC.
www.mikebeganyi.com
Re: Principal Rafter Tie Connection #25079 01/08/11 03:31 PM
Joined: Mar 2002
Posts: 961
K
Ken Hume Offline
Member
Offline
Member
K
Joined: Mar 2002
Posts: 961
Mike,

Why would the top of the post shear in a housed joint when more than the full section of the post is available to handle shear ?

Regards

Ken Hume


Looking back to see the way ahead !
Re: Principal Rafter Tie Connection [Re: Ken Hume] #25080 01/08/11 05:11 PM
Joined: Jan 2008
Posts: 918
B
bmike Offline
Member
Offline
Member
B
Joined: Jan 2008
Posts: 918
Ken -

I've had to design around issues where the post above the tie beam is a lever arm, and the thrust from the rafter wants to shear the post off at the tie, as it is assumed the tie is doing its job and resisting the tension. This type of configuration can be tricky to get right - its a balance of having the tie close enough to the rafter, but still far enough to leave enough meat for joinery. I can post a sketch when I get back into the office as I can't seem to attach anything from my mobile.


Mike Beganyi Design and Consulting, LLC.
www.mikebeganyi.com
Page 1 of 2 1 2

Moderated by  Jim Rogers, mdfinc, Paul Freeman 

Newest Members
Bradyhas1, cpgoody, James_Fargeaux, HFT, Wrongthinker
5137 Registered Users
Powered by UBB.threads™ PHP Forum Software 7.7.3
(Release build 20190728)
PHP: 5.4.45 Page Time: 0.143s Queries: 17 (0.108s) Memory: 3.2185 MB (Peak: 3.3987 MB) Data Comp: Off Server Time: 2024-05-17 13:49:47 UTC
Valid HTML 5 and Valid CSS