Ideally the forces are resolved in the bottom chord by landing the toe of the strut well inside the post to develope the required shear planes. Of equal concern is compression load at the top of the queen ties. Also consider braces under the bottom chord. In matters of truss design, get an engineering review.
|
|
|
Re: Flat timber truss
#26821
07/19/11 12:28 PM
|
Joined: Jul 2011
Posts: 3
Scott Beaumont
OP
Member
|
OP
Member
Joined: Jul 2011
Posts: 3 |
Roger - thanks for the reply. I am a structural engineer (I work with a building components company) I am reviewing this truss design and I am looking for some field knowledge of this truss as I have never designed it before.
The magnitude of the tensile/compressive loads in the truss arrangment (approx. 25,000 lbs) are proving problematic to resist with dowels in double shear. My span is 24' (28' trib width) with a 44 PSF factored snow load. The literature I referenced mentions spans up to 60', so there must be a strategy for this design.
I was thinking the compressive loads are of less concern becuase I will have wood on wood interaction and can use this to assist with load transfer at the joint - comments?
For the tension joint we are discussig, I have 12x12 white pine members w/ red oak dowels. My preliminary calculations indicate that I will require 25 dowels to resist this tension. I suppose I could use a knee brace to add additional tensile strength at the joint as you suggested.
Any other thoughts. Thanks again Roger.
|
|
|
Re: Flat timber truss
#26822
07/19/11 12:36 PM
|
Joined: Jan 2008
Posts: 918
bmike
Member
|
Member
Joined: Jan 2008
Posts: 918 |
Can you post up a sketch or two? I'm not sure which image in that PDF you are referencing.
And, in many cases, folks use steel connections for the tension loads. Lots of ways to take the compression loads with wood to wood joinery, sometimes backed up with lags or through bolts to hold things together (adding in a mortise and tenon may actually weaken areas of timber where you just need brute surface area.
|
|
|
Re: Flat timber truss
[Re: Scott Beaumont]
#26823
07/19/11 01:51 PM
|
Joined: Oct 1999
Posts: 463
Roger Nair
Member
|
Member
Joined: Oct 1999
Posts: 463 |
Mike, I think it's fig. 4.
Scott, in timber framing design heavy load transfer should occur in the abutting surfaces of the joints not by dowels. Issues exist in the difference in bearing capacity of end grain to side grain such as might happen at the top of the queens where the end grain of the strut and the end grain of the top chord pinch the side grain of the queens in a everlasting grip.
Last edited by Roger Nair; 07/19/11 01:59 PM.
|
|
|
Re: Flat timber truss
#26824
07/19/11 02:08 PM
|
Joined: Mar 2010
Posts: 14
KBLanier
Member
|
Member
Joined: Mar 2010
Posts: 14 |
post a picture of the design your considering. I am interested in your design. I always like to see what others are doing.
|
|
|
Re: Flat timber truss
#26825
07/19/11 03:20 PM
|
Joined: Nov 2003
Posts: 687
Gabel
Member
|
Member
Joined: Nov 2003
Posts: 687 |
It is typical in modern timber framing for any significant tension connection (in our work this means anything over 2 kips) to employ steel whether it be side plates (not my preference), knife plates, barrel connectors, or any number of other schemes.
It is possible to design a solution to the problem, but in this case, I would try to design the problem away.
In historic examples, as Roger points out, these types of connections were avoided by configuring the truss or frame to use compression joints only (sometimes easier said than done). In my simplified view, I think in terms of making the truss to be self supporting, where it just sits on top of the supports rather than having it pulling or pushing on the supports. This sometimes requires designing the truss to be a separate, complete component rather than integrated into the supporting structure.
For some historic examples of how the joinery was configured in parallel chord trusses, look at covered bridge truss designs.
I hope some of this helps.
|
|
|
Re: Flat timber truss
[Re: Scott Beaumont]
#26828
07/20/11 02:26 AM
|
Joined: Jul 2011
Posts: 3
Scott Beaumont
OP
Member
|
OP
Member
Joined: Jul 2011
Posts: 3 |
First of all, thanks to everybody for sending me their feedback. I am interested in hearing potential solutions to the joinery issues I have.
I am trying to post a sketch of the design so you can see what it looks like but I can't seem to figure it out. The FAQ says to use the file manager which I can't find anywhere.
Any suggestions so I can post the PDF file?
Thanks.
|
|
|
Re: Flat timber truss
#26829
07/20/11 03:23 AM
|
Joined: Jan 2008
Posts: 918
bmike
Member
|
Member
Joined: Jan 2008
Posts: 918 |
You will need to post the file on something like DropBox or Google docs. Then share a link here.
|
|
|
Re: Flat timber truss
[Re: Scott Beaumont]
#26831
07/20/11 11:34 AM
|
Joined: Jul 2011
Posts: 3
Scott Beaumont
OP
Member
|
OP
Member
Joined: Jul 2011
Posts: 3 |
[img:center] https://docs.google.com/viewer?a=v&p...M0&hl=en_US[/img] This drawing is a rough sketch of the proposed frame. The ridge truss is used to support the floor beam via steel rod in a gable style 24'x28' attached garage. From the sounds of it, I will need to use steel to connect these members. Is there a way to conceal the steel connections?
|
|
|
|
|