How much can purlins reduce the size of rafters ? #38 06/26/99 05:09 PM
Joined: Jun 1999
Posts: 5
T
tedd Offline OP
Member
OP Offline
Member
T
Joined: Jun 1999
Posts: 5
I read in FHA (old) publication of timber framing/pole construction that 2X8 rafters (30" OC)and 2X4 horizontal purlins (35" OC) will adequately span between 14 to 15" in moderate snow load country. Any info out there on light construction spans like this - code acceptance, realistic replacement for 2X12"s ? Also, wwaht size must girder headers be to carry this load across 12' pole span ?

Re: How much can purlins reduce the size of rafters ? #39 06/27/99 10:59 AM
Joined: Aug 1998
Posts: 56
B
Brian Wormington Offline
Administrator
Offline
Administrator
B
Joined: Aug 1998
Posts: 56
Tedd:

I assume you mean 14-15 feet, not inches for the span.

The situation you are describing sounds like one in which the purlins are supported by the rafters rather than vice versa. In this case the total load carried by the rafters will be the same as in the case with no purlins, Thus, the purlins don't reduce the work that has to be done by the rafters. Rather, they simply give more points at which the roof deck can be attached.

In barn roofs, there is often a purlin plate which supports the rafters at mid-span. In this case the distance spanned by the rafters is halved and thus permits them to be smaller and on a wider spacing.

It's not possible to answer your girder question without knowing the actual loads, but in timber-framing 12 feet is a common span and often supported by normal-sized plates.